Mr Hehound
Bit stumped.
Went to look at a florescent light in a garage that was flickering.
Checked voltage at fitting - voltage ok.
Had a spare tube and starter in the van and stuck this in after removing the old one and seemed to work fine.
Another call - light has started flickering again.
Traced circuit back (looped from living room lights which is next door to garage) test continuity, ir and zs - all ok. Also made sure terminations were tight.
Thought it must be the balast. As it was an old fitting, changed it for a new one without a starter. Tested it, turned it on and again was working ok.
Amother call today. Light had again started flickering and then stopped working completely.
tested voltage again (still there) and tried connecting a pendant up which worked fine.
Put the tube back up - still doesnt work.
Customer said they have had a recent leak in the bathroom which is above the lounge in which the garage light feed is taken from but theres no sign of water in either the lounge or garage fittings.
Bit stumpted now.
What are the chances i've had a faulty tube followed by faulty new light fitting. If it was that, why did thet initially work then stop?
What am I missing here?
Any help gratefully recieved (fault finding is good fun but can be frustrating at times)
Went to look at a florescent light in a garage that was flickering.
Checked voltage at fitting - voltage ok.
Had a spare tube and starter in the van and stuck this in after removing the old one and seemed to work fine.
Another call - light has started flickering again.
Traced circuit back (looped from living room lights which is next door to garage) test continuity, ir and zs - all ok. Also made sure terminations were tight.
Thought it must be the balast. As it was an old fitting, changed it for a new one without a starter. Tested it, turned it on and again was working ok.
Amother call today. Light had again started flickering and then stopped working completely.
tested voltage again (still there) and tried connecting a pendant up which worked fine.
Put the tube back up - still doesnt work.
Customer said they have had a recent leak in the bathroom which is above the lounge in which the garage light feed is taken from but theres no sign of water in either the lounge or garage fittings.
Bit stumpted now.
What are the chances i've had a faulty tube followed by faulty new light fitting. If it was that, why did thet initially work then stop?
What am I missing here?
Any help gratefully recieved (fault finding is good fun but can be frustrating at times)