Hi there went a job today to supply a light box for a shop today, it has 30 fluorescent tubes inside it done the cable calc 30 x 58watts = 1740
1740/240=7.25
So I fitted a 10amp rype b mcb and it tripped so I clamped the load going out it was reading 10.8amps and on start up it was hitting 11-12 Amps.
Now I'm thinking of fitting a 10amp type c mcb will this do it
Has anyone come across this??
 
C type should be OK but you need to check your Zs is suitable for the MCB.

What do the manufacturers recommend?
 
Firstly can I ask if you are electrically competent and/or qualified to carry out this work ?, I ask because I would like to know if you have established the cable sizes and protective device characteristics required for this load.
J
 
Depending on the type of light you need to take into account the load of the ballast, if appropriate or the HF unit. Also the power factor will also conspire to increase the current above the basic calc of adding up the tubes and dividing by the voltage.

With a tube load of what you have described i would have put it on a C16 on 2.5sqmm cable, depending on cable length.
 
The box is pre wired in 1.5mm t + e, I run in a 1.5mm fp cable 10 metre run to the first connection done r1 + r2 at the furthest point all good turned it stuck a clamp metre on the load side with it reaching 10.8 amps.
 
this is what i think delboy needs to do.

Find out how many lights this circuit is supplying.
determine the cable size and length
do a r1 r2 test on the circuit. every point.
last point will be the highest
If it higher somewhere in the middle then yes u may have a loose connection
do a live test ze at the board
do a live zs test at the last point
This will give you ur zs
if its below 1.84ohms then bang a 10 amp type c

jobs a good'un
 
What about if you use the R2 method?


I always record the highest reading.

Agreed on a ring with spurs, with a Radial how can a higher reading be anywhere except at the end unless you have a fault or an external influence ? If you have done the r1 stuff first, I fail to see how the impedance can be higher mid circuit than end circuit on a Radial ?
J
 
Just a personal preference, but checking every point ensures all current using points meet the required Zs rather than relying on a installation being perfect because one other test says all is good.
 
The run is 10 metres mate what do you think I can easily change the wiring to 2.5mm for a c16 or change the mcb to a c10.

A C16 can run on 1.5 if you can get the right ZS readings for it. Fitting a C10 is high risk if its running 10.8 now, you could well be back after tripping in hot weather assuming it stays in long enough for you to leave the premises.
I cannot say because i dont know you total cable run through the switches and the Zdb.
What i do is (before ordering cable) measure Zdb stride the cable run for an idea of cable length then over a coffee decide how many circuits and how fat a cable to use.
You wont get a definitive answer here because your variables are unknown, but i would be surprised if you cannot make it work on a C16 and 2.5, as you have run the cables, if your ZS at the end of your run is less than 1.16ohms than fit a C16, if its greater then oops,
 
The correct method for calculating the protective device is as follows.

30 x 58 x 1.8 = 3132 W

3132 Divide be 230V = 13.61A

The protective device should be 16A

The normal type this type or lighting should be type C.

Cable calculations should be based on a load of 13.61A
 
As the others have said, check your Zs at the end of line (should be the highest) and just make sure it doesnt exceed the maximum value given for the mcb you require. (in this case a Type C)
If it does exceed that value, how about changing for an rcbo? Or reduce the earth loop impedance by adding supplementary bonding (if practical)
 
As the others have said, check your Zs at the end of line (should be the highest) and just make sure it doesnt exceed the maximum value given for the mcb you require. (in this case a Type C)
If it does exceed that value, how about changing for an rcbo? Or reduce the earth loop impedance by adding supplementary bonding (if practical)

Or carry out cable calculations and get it right first time.
 
As the others have said, check your Zs at the end of line (should be the highest) and just make sure it doesnt exceed the maximum value given for the mcb you require. (in this case a Type C)
If it does exceed that value, how about changing for an rcbo? Or reduce the earth loop impedance by adding supplementary bonding (if practical)


Why do electricians need to be reminded of this stuff time after time?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fluorescent tube light help
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
41
Unsolved
--

Advert

Thread statistics

Created
Delboy247,
Last reply from
steveberry11,
Replies
41
Views
3,921

Advert

Back
Top