I concure. Most electricity Suppliers REQUIRE an isolator and cutout if the "tails" are more than 3m in length. I believe also that the regs, in a roundabout way, required a cutout (fuse, MCB etc. etc) if the cable size changes, and you will shorly be comming down from 25mm to 16mm. Also note that some suppliers also required a bonding cable in Cu all the way beack to the MET.
 