Hi I’m still doing my apprenticeship, and I was wondering if you guys can help me.
There are 2 flats, one above the other.
Both gas meters are side by side out the front of the ground floor flat.
The gas bond for the ground floor flat has taken the 10mm earth cable from the CU to the gas meter box and bonded, it then continues to the gas meter for the top floor flat and bonded (with no break in cable).
The top floor flat has a 10mm earth cable from its own CU to the gas pipe within 600mm of point of entry of the dwelling.
In short this means that both CU’s are earthed to the same gas pipe. Is this acceptable.
 
Hi I’m still doing my apprenticeship, and I was wondering if you guys can help me.
There are 2 flats, one above the other.
Both gas meters are side by side out the front of the ground floor flat.
The gas bond for the ground floor flat has taken the 10mm earth cable from the CU to the gas meter box and bonded, it then continues to the gas meter for the top floor flat and bonded (with no break in cable).
The top floor flat has a 10mm earth cable from its own CU to the gas pipe within 600mm of point of entry of the dwelling.
In short this means that both CU’s are earthed to the same gas pipe. Is this acceptable.
are the mains boards for each flat from one supply or are there 2 incoming suplys

the regs state that in each installation main protective bonding conductors complying with chapter 54 shall connect to the main earthing terminall , so following your question if the electrical supplys to the flats are seperate that would make two seperate installations so there for you would have to earth the gas back to the main earthing terminal , if the upstairs flat is a sub main from the down stairs then i suppose the you could argue its one installation then it would be ok.
 
Last edited by a moderator:
In each installation main protective bonding shall connect to the met
Where an installation serves more than 1 building the protective bonding to the gas should be applied to each building
This implies to me that whether there is seperate supplies or just the one then the gas earth should be installed for each flat from its own dist board to its own point of entry(not outside in the box)
I would remove the link so that the equipotential zones remain seperate and no I do not think it is acceptable
 
What are the mains supplies to the flats ??? pme ? If so are there 2 supplies ie 1 to upstairs 1 to downstairs ?
If 2 seperate supplies i agree no need for link.
If sub main to the top floor flat, does this still make the top floor flat a pme supply - i dont think so.Then different regs apply.You would need to look at the nic tech manual.
 
I would say that each flat should have its own MET and bonding to its own meters.

This would safe guard the second flat against lack of gas bonding should the first flat ever have the gas cut off and the meter removed.
 
Hey.

The last block of flats I did, we ran seperate bonding conductors from each flat down to each gas meter in the basement, in 16mm just to be safe and also the same with the water services.

The services were also bonded at point of entry to each flat incase of any breaks in pipework at later date.

Overkill? maybe.
 
Last edited by a moderator:

Reply to Gas Bonding in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
287
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi, went to have a look at a job today, customer has had gas supply company out (for another issue) and they have commented that the protective...
Replies
1
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock