Dizzy_Maskell

Guys,

We did an EICR on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in Tarmac and all cables to these various buildings fed from a main sub are SWA cables using the armouring as the earth

The issue is that all out buildings etc the earth loop impedance is too high.

The earth loop in the Sub is fine but due to length of run etc the earth loop at all the boards is too high.

We have advised the site about this and explained they need to run separate earth to each out building with the cable.

They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the Tarmac to each building,

How he plans to do this we are yet to hear but I think I can hear a yeeeee haaaaaaa in the horizon
 
Numerous to be honest and quite a variety earth loops also ranged quite a lot I think most where to high by about 1-2 Ohms
 
Sounds more like a high reading inside the buildings than the Zdb readings. What were the R1+R2 readings like?
 
Numerous to be honest and quite a variety earth loops also ranged quite a lot I think most where to high by about 1-2 Ohms
is it high though? is the mains to the units fed from a board which makes them circuits and therefore the readings may be nt so bad? anyhow whack a rcbo in and forget all about it :smilielol5:
 
Issue we found that the earth loop to high for the over current protective devices, So needs improving to comply with manufacturers guidelines
 
Have you got the R1, R2 and Rn readings to prove that it is even possible to lower the readings enough by installing an additional cpc.
 
Also don't want to use RCD as some of these out building are used as mini sub mains feeding further areas, Bit of a chain affect but the high earth loop begins to affect DBs further down the line
 
Yes we proved this and an additional earth would resolve the issue but the client refuse to dig up the site to fit earths.
I think also some of the cables needed an additional earth any way due to their size but this was never installed initially.
Just amazed to hear that a earth ring was a possible idea for an entire site
 
I'm a bit confused about these threads. Why is one spark doing the work and another (you) doing the EICR?
 
I'm presuming its MCCB's or BS-88 as means of protection in the main sub? It sounds like their installation was originally poorly designed with little or no thought into cable factoring/volt drop/etc.

Maybe easiest method is to turn into TT and rod each unit with RCD protection?
 
You seem a bit unsure about what you're saying, there are a lot of 'I think's in there!

What type is the main DB?
 
They got an independent company do their EICR and have their maintenance do remedial work. Yes the original install is poorly designed.
We suggested earth rods and TT but again don't want to dig so insist can run earth ring on floor and just tap into it seems crazy but their electrician thinks its a great idea I think it is riddled with complications though
 