Dizzy_Maskell
Guys,
We did an EICR on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in Tarmac and all cables to these various buildings fed from a main sub are SWA cables using the armouring as the earth
The issue is that all out buildings etc the earth loop impedance is too high.
The earth loop in the Sub is fine but due to length of run etc the earth loop at all the boards is too high.
We have advised the site about this and explained they need to run separate earth to each out building with the cable.
They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the Tarmac to each building,
How he plans to do this we are yet to hear but I think I can hear a yeeeee haaaaaaa in the horizon
We did an EICR on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in Tarmac and all cables to these various buildings fed from a main sub are SWA cables using the armouring as the earth
The issue is that all out buildings etc the earth loop impedance is too high.
The earth loop in the Sub is fine but due to length of run etc the earth loop at all the boards is too high.
We have advised the site about this and explained they need to run separate earth to each out building with the cable.
They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the Tarmac to each building,
How he plans to do this we are yet to hear but I think I can hear a yeeeee haaaaaaa in the horizon