It's a Schneider MCCB board but that taps off to some BS88 fused isolators from the incoming side so mixture very old install needs an overhaul really
 
Don't worry about it, it's not your problem. If you're happy with the EICR you/your firm did, then who cares how they choose to act upon it?
 
Because we will be going back as they have advised they want annual EICR until site is satisfactory bit of a nightmare as it is 1 site of a clients we do a lot of work for so need a good relationship and the maintenance managers want out opinion on this remedial work.
As it goes against what we originally asked but they are saying is a suitable alternative
 
Ok guys so all other issues aside what are people's take on a huge cable being ran around the perimeter of the site and being cut and tapped into at various points,
To form a "site earth ring" just sounds so dodgy to me,
bear in mind it takes about 20 min to walk the site perimeter it's gonna be massively long and have to be so big it seems stupid
 
Leave it upto the customer, then next year see what the results are from it, whether it contravenes any regs.
 
Calculate the load, drop the overcurrent device which feeds the armours?
New max zs reading ok?

Boydy
 