Guys,

We did an EICR on an entire site a few weeks ago the site consists of numerous out buildings, sheds, maintenance shops etc. The site is entirely covered in Tarmac and all cables to these various buildings fed from a main sub are SWA cables using the armouring as the earth

The issue is that all out buildings etc the earth loop impedance is too high.

The earth loop in the Sub is fine but due to length of run etc the earth loop at all the boards is too high.

We have advised the site about this and explained they need to run separate earth to each out building with the cable.

They have come back to us today after their electrician has said he plans to run an earth ring around the perimeter of the site tapping in to each building as required instead of digging up the Tarmac to each building,

How he plans to do this we are yet to hear but I think I can hear a yeeeee haaaaaaa in the horizon


The main problem here, is that using the SWA armour as the sole CPC to an out building, is that the SWA CSA will generally not comply, if it is also going to be used for that buildings bonding requirements. That will generally require full sized additional core of a SWA cable or a full sized separate core. If the DNO's supply is TNC-S/PME then additional requirements may need to be applied!!


Another point to make here, is that trying to TT these Tarmac surrounded buildings is going to be a thankless task unless you're going to make provision to keep the rods or electrodes damp. Nothing worse, than a dry soil environment to provide for a working TT system!!
 
Last edited by a moderator:
i woz trying to make that point in another post and woz laughed at by idiots


That's because you didn't really know what you were talking about!! Same here too by the looks of it, as you have left out the very reason ''Why'' it won't comply from the cropped quote you made!!
 
i woz trying to make that point in another post and woz laughed at by idiots

You've altered the quote from E54 to make it look like he has said something he hasn't! Are you a journalist or something?

He was saying that the SWA generally won't comply for main-bonding requirements, not that it won't comply as a CPC.
 
I am..... he told me so!!!
I think he was.. (sorry woz) trying to say Trev was also on his "list"
Does that mean I can insult him without him knowing!! :wink5:
That he is ignoring me neither comes as a shock or bothers me, the guy is a clown and appears to have delusions of adequacy.
If you're on his list and insult him he can find out about it if someone not on his list quotes you :)
 
des, did you know you'd won the guess the Ra thread?
 

OFFICIAL SPONSORS

Back
Top