I have an Accenta Gen 4 panel and Guardall PQ15 pirs.
I have wired the pirs to panel as follows:
On pir + to 13v on panel.
On pir - to 0v on panel.
On pir NC alarm to zone on panel.
On pir NC tamper to TAMP on panel.
The other terminals on the pir are not connected are:
Test
Ctrl
NC Aux/Fault
Can anyone please confirm this is correct or let me know the right way.
 
Your 2 NC connections on the PIR should go to the relevant circuit pair on the panel; the tamper pair on the PIR to the tamper pair (or global tamper pair) on the panel).

Regards.
 
you have to wire all your tamper loops in series and connect th 2 ends into tamp.
 
Your 2 NC connections on the PIR should go to the relevant circuit pair on the panel; the tamper pair on the PIR to the tamper pair (or global tamper pair) on the panel).

Regards.

You have confused me now :-)
Just realised that I put the connectors wrong on the forum, they are as follows:
1: On pir + to 13v on panel.
2: On pir - to 0v on panel.
3 & 4: On pir NC alarm to zone on panel (2 connectors)
5 & 6: On pir NC tamper to TAMP on panel. (2 connectors)
The other terminals on the pir are not connected are:
7: Test
8: Ctrl
9 & 10: NC Aux/Fault (2 connectors)

Would you be able to help in simple terms to help me please
 
What you have described is correct , noting the post from Telextric that if you have other detectors/contacts with tamper circuits, you connect all the tamper pairs in a "daisy chain" to the global tamper circuit on the panel (i.e. you have the first leg of the first tamper pair and the second leg of the last tamper pair connected at the panel aka "in series").

I noticed your earlier post - the programming can be a bit off-putting on the Accentas if you are not used to them - double check the programming of circuits before you walk test again.
 