be fair, glenn, it sounds like an awkward fault that didn't show up before the CU change. could be something glaringly simple, but he's having a blonde one.
 
well for a start if its only doing it when loads are connected then this suggests a neutral-earth fault...
further more if its when he turns on any light.....this suggests something near the board...
 
Y can't i see Glenn's comments?! :-/

Tel, no didn't show up on Pre testing!! Now I'm in it!! Lol!
 
When your testing your rcd are you doing it with your 3 leads at the board or at a socket?
 
Murdoch - pme, 0.78 (if memory serves me) !! Good reading... That's not the 'end of' the circuit though (there isn't one) must be under floor in jb for a wall light.... Somewhere!! :(
 
Onions... Sockets on other RCD, for this RCD currently controlling up and down lights (2sep circuits but temp on same RCD) have tested at 4 points -one upstairs, 2 down, and at mains and none are tripping <35mA!! :(
 
Have you not disconnected 1 of your lighting circuits and narrowed it down to the upstairs or downstairs being the problem?
 
Onions... Sockets on other RCD, for this RCD currently controlling up and down lights (2sep circuits but temp on same RCD) have tested at 4 points -one upstairs, 2 down, and at mains and none are tripping <35mA!! :(
ramp it....
 
Onions, yes just downstairs.
Glen I have ramped it and it's >35mA at 0d and 180d?! Puzzling the hell out of me!! On paper there's nothing wrong?! Test results etc but RCD just won't have load!! :(
 