Heat Alarm Position

Hi, quick question. I installed an Aico system among other things in a HMO 5 years ago. The kitchen is pretty standard size approx 5m by 5m. The Aico heat was installed not far from the doorway about a metre in due to the criss crossing nightmare joists. Now the client has had a HMO inspection and been told that the heat is in a bad position and should be moved closer to heat sources. Now I have never heard this before and wanted to run it by the forum and see if it is indeed a thing. I'm being a bit lazy but really cannot be arsed to trawl through building regs. Thanks in advance
 
If you are installing fire alarm systems I presume you have BS5839-6.
 
If you are installing fire alarm systems I presume you have BS5839-6.
Hi yes I do have BS5839-6 and I have admitted to being a bit lazy and coming straight to the forum. From what I remember the distance from any heat source was 5.3m, and the kitchen being 5m in length and the heat 1m inside the room I would have thought that it was well within the required distance
 
Just for info on this post, I've fitted heat alarms in small kitchens before now and when they open the oven door it sets the heat alarm off, this has happened on more than one occasion in the past, so to say move it closer to the heat source is stupid. Obviously pen and paper men have never worked in the real world.
 
Aico used to stipulate in their instructions about the position of heat alarms. Think it was 1.5 m laterally from the heat source. Their technical helpline is very good.
 