I would like to fit some heat resistant uplighters inside a chimney brest low level. These would be about a foot off a stove. Does anything suiutable exsist. I was going to wire in fp200 and sleeve the core with heat proof sleeving also. Any help appreciated
 
I did something similar with a GU10 spot light once. FP200 to the fitting (all metal, designed for the heat from the lamp) crimped the connection and covered with heat proof sleeving and used a 35w halogen bulb (!) as heat is their thing. Put it on it's own dimmer too as the light was for effect more than anything

Customer loved it
 
the first thing here is to measure the ambient temp where cable and fittings will be when stove is on, then from there id design the install, and Fin170 i get what you say regarding the gu10's but you need to remember the lamp has to dissipate its heat away and if ambient temps are too high you will effect the lamp life.
As the O/P is saying they will be low level under the stove its possible this wont be an issue as the heat dissipating from the stove will rise pulling in airflow from the room but as i said just getting a temp reading gives a good start point to this design.
 
There isnt a stove in place yet, so struggling on temp measuing. but they will b low level so shouldnt get as hot.Thanks for yuour help.
 