Thanks, just had a quick look at a cu change,
Will post pic when get home
Grand floor sockets on ring then someone has spured of taken up stairs made up some sort of ring ish gone back to cu then at mcb called it upstairs downstairs ring all on a 32 amp mcb,
29 13amp 2 gang , and about 6 spurs, but thay have some things in the loft ( boiler, lights train set) which is all of same mcb, going back in morning to do full test but I think it mite need a full rewire whot do you think
 
I think there are other cheaper ways of resolving this pigs ear other than rewiring it into two circuits. With not a great deal of work it should be possible to trace all the legs and reroute them into an RFC for each floor.
 
agreed. once you mfind what goes where, it might be relatively easyt to divert a leg here and there and add a bit of 2.5mm to make it into 2 RFCs or an RFC (downstairs) and a radial (upstairs)
 
Yes I was thinking that naw I'm siting at home with nice cold beer, got some pics but can't put them on will keep trying, think the upstairs RFC is hiding under floor and thay have used JB s but will take floor up when testing tomorrow,
Not all floor just a nuth to see whirs going on
 
Think I've had too much to drink looking at the spelling on that last post
Still trying to post pics will keep trying but it could be a good time to go meet someone in the pub before the wife gets home
 
Sorry it's taken so long but had problems putting pics on
Had a look up floor upstairs and can make radel in to ring without too much work all rooms are going to be re painted, and new carpets going down
And have been asked to change the DB
Happy days
 

Attachments

  • image.jpg
    image.jpg
    165.3 KB · Views: 45
  • image.jpg
    image.jpg
    130.3 KB · Views: 54
what a bloody abortion.
 
Two -way switch in hall, don't think it's a Electrical Trainee, it's a 2 day try it and see if it works
 

Attachments

  • image.jpg
    image.jpg
    93.6 KB · Views: 50