Hi everyone .pleased to find such forum where I can get help and advice.ive done my 236 , 17th edition .and 2392 testing.but not doing electrical as profession. So all ways need of professional advice from experienced .hope to enjoy this.
Here is the first one I need help with .
Iam testing a floresent fitting .
What test result would I expect on IR test of floresent fitting.ive tested them individually. Some are over 1 mega
Others are 0.03 M oms.
 
Do you mean a "Fluorescent" light fitting?
If so, would be an odd thing to IR test it, especially at 500v between line & neutral. As for "what test results would I expect" the answer will probably be, that they no longer work.
 
Are you IR testing flourescent's individually....Are they all on there own circuits?

Make sure the tubes are out, obviouslly. Then anything under 2meg needs rectification. (1meg according to gn3, but most of us work to 2meg)
 
Do you mean a "Fluorescent" light fitting?
If so, would be an odd thing to IR test it, especially at 500v between line & neutral. As for "what test results would I expect" the answer will probably be, that they no longer work.


thanks for your reply.luckly they are still working .please tell me how to test flourescent light fittings
 