I've just remembered that Lenny has posted a very good cable calculation method on here somewhere, if you search for it, it's well worth it.
 
Just looked at your thread again, are you sure about the domestic storage heater being 14000 watts?????
Think you may have put the decimal point in the wrong place!!!!!!!!
 
Oh sorry, I see what u mean. It defo says 14kw. Guess it could be a typo error. 1.4 would be eaiser to work out wouldn't it?.
 
If the question asked for 14Kw then work it out on that, you can't go wrong of they have provided the wrong information. Must be a warm house... :lol:
 
I've tried working it out but can't seem to get the z's below the max z's. I can work it out using 1.4kw
 
"If the question asked for 14Kw then work it out on that, you can't go wrong of they have provided the wrong information. Must be a warm house... :lol:"

Definately would not like the bill for that house.:)
 
Your training provider may or may not get this right, but the BS3036 factor of 0.725 (which is due to the higher fusing factor) is not to be used in this circuit. This is because the load is not subject to overload.
 
I'm pretty confused now to be honest. So can it be worked out on 14kw???, cause I can't do it and keep it below the max z's.
 
I'll have a play with this at work tomorrow as thats where my regs is. If the question has been given in a way that it cannot be properly resolved, I will adapt it to comply so you can take it back to your tutors. :p
 