In theory, if the Source Earth and Additional Source Electrode failed in a TN-C-S, as the earth and neutral are combined, could they both become live and all your bonding metal work pose a shock hazard?
 
Exactly . With a TNCS system the neutral and earth are combined , at the customers cut out , because of the dangers off a break in the neutral back to the transformer , there are multiple earth points installed along the route, because otherwise the return current would flow back through the bonding pipework and then off course you would have 230V potential on the neutral as well, But with everything in tact the 230V potential on the neutral is the same as the electrical earth
 