I have a practical exam on Thursday and have just found out I have to perform a test that I haven't yet covered(my own bloody fault)
So at this late hour I am getting a bit concerned.
I have a length of SWA 2.5mm 3 core wired into a CU at one end and an isolator at the other.
Could someone please explain simply to me how to perform 1,Continuity 2,Ins Resistance and 3,Polarity on the SWA
I have some idea but with a million thigs running through my head I need some help.

Thanks in advance

Gerry
 
Isolate cu

1)remove conductors from cu terminals
2) connect line to cpc of swa & test continuity at the load side of isolator between line & cpc, turn isolator on/off while testing prooves line is switched (R1+R2 done & polarity)
3) remove link between line & cpc
4) set meter to 500v test IR between line & cpc
5) test IR between neutral & cpc
6) test IR between neutral & cpc
 
Isolate cu

1)remove conductors from cu terminals
2) connect line to cpc of swa & test continuity at the load side of isolator between line & cpc, turn isolator on/off while testing prooves line is switched (R1+R2 done & polarity)
3) remove link between line & cpc
4) set meter to 500v test IR between line & cpc
5) test IR between neutral & cpc
6) test IR between neutral & cpc


Thanks very much,very helpful

I see that steps 5 and 6 are the same,should step 5 be test IR between line and neutral.

Either way thanks again!
 

Reply to Help Please! in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
677
Hi , I just started my designh project 2365 level 3 for hotel building. I have dyslexia I don’t know where to start can anymore done it before he...
Replies
4
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
391
Guidance please - C&G L3 electrical installation - Hotel extension project Hi folks, I am fairly new to this forum but it looks like the...
Replies
6
Views
579
Good evening everyone Can any help or give me some advice please on measuring bending galv conduit. My question is bending long 3m lengths...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock