I'm an apprentice and have a practical exam tomorrow.
i have to terminate MICC, SWA, SY etc...

The only thing I need to know is what you do with the earth tag which sits on the gland on the end of each cable.
Which earth cable do you use? And how do you connect it to the earth tag?
 
Don't you think you have left this a little late in the day to be asking questions like this? Your best thing to do is look on you tube so you can actually see it
 
Don't you think you have left this a little late in the day to be asking questions like this? Your best thing to do is look on you tube so you can actually see it
I've looked on YouTube and watch termination videos for SWA and SY but they never show what you do with the earth tag?
 
What have you used previously when you have practised terminating these cables?
We have been shown how to gland off with the earth tag, but we haven't been shown what to do with the earth tag once the gland is mechanically safe
 
Well, before the assessment starts talk to the tutor and ask them what they expect you to use. They will know the resources that are available and should tell you.
 
Must admit, I'd be a bit baffled too............with MICC.

Not needed, if a normal glanded termination is being made to a metallic enclosure, unless the tails are being extended through a metal box/enclosure to a plastic enclosure. Only ever seen them used when being glanded to a plastic box/enclosure, or were no gland is being used and only the pot is being gripped as in made for purposes MICC back boxes.
 


Not needed, if a normal glanded termination is being made to a metallic enclosure,
unless the tails are being extended through a metal box/enclosure to a plastic enclosure. Only ever seen them used when being glanded to a plastic box/enclosure, or were no gland is being used and only the pot is being gripped as in made for purposes MICC back boxes.
thank god for that..

at last someone has stated the bloody obvious...
 


Not needed, if a normal glanded termination is being made to a metallic enclosure, unless the tails are being extended through a metal box/enclosure to a plastic enclosure. Only ever seen them used when being glanded to a plastic box/enclosure, or were no gland is being used and only the pot is being gripped as in made for purposes MICC back boxes.

Just the point I was making......read it wrong, I think.