So I guess that if i'm going for these LED's and only using 6 of them with a time clock then I'm not going to need a contactor am I?
 
You will probably need a type C mcb, i installed 3 led floods and the initial inrush tripped a type B for some reason, maybe someone could enlighten me why?
 
So I guess that if i'm going for these LED's and only using 6 of them with a time clock then I'm not going to need a contactor am I?

I think I'd probably still fit a contactor. The timer and photocell will last longer when there switching minimum load.
 