If it has the correct size heaters then a greater diversity factor will come in to play as the thermostats will cycle correctly.
As for the emergency lights, is the customer suitably qualified to make that decision? Do you understand why putting them on a seperate circuit may be a bad idea which you, as the installer, could be liable for?
Have you ever carried out a load study on a domestic property? Or even measured instantaneous current draw with a clamp meter?
An old lecturer told me don't worry too much as at worst it'll just blow the main fuse but I'm not entirely comfortable with that response
Great advice that. 'Don't worry if demand is a bit too high, it will just knock out the entire system and need the DNO to come and fix it'. Makes you wonder why we bother working max demand out really. Daz
Hi dave this is the first time I have been asked for emergency lighting I've checked onsite guides and it didn't mention anything about them been on either a separate circuit or the lighting circuit, I just did it on a separate circuit for identification on the cu
would I be ok to connect the emergency lighting into the same mcb as the downstairs lights if they don't pull much power?
sorry to ask so many questions but these two topics (emergency light and demand) I've not had issues with in the past
cheers mark
i know daz and I'm finding it difficult to find the answers I need
cheers mark
Think about it. Emergency lighting is there to be activated and provide lighting when the main lighting fails.
Reactions: 2 people
cheers mark
But how does the emergency lighting know to come on? Daz
Sorry Andy, your post wasn't there when I typed :-) Daz
i understand but each floors as its own circuit and the hall and landings have their own circuit so could I join the hallways and emergency lighting feeds into the same mcb save me having to go back and re wire?
As designer and installer, how you achieve the requirements for emergency lighting is up to you.
Hall stairs and landing are on their own as I've been asked to fit the pneumatic switches so when one is pushed all the lights on all the hallways come on the way that they had to be wired are a direct N feed from the CU into the fitting and line and switch line into switches
I'm assuming here you mean intermediate switching
cheers mark
Are you sure you are competant to design an emergency lighting installation then?
They need to be connected to the lighting circuit serving the area they are in, otherwise how do you expect them to come on when the normal lighting fails?
No, the emergency lights need to be connected to the lighting circuit serving the area the are fitted in. Otherwise they will not operate when the lighting circuits fail!
I wouldn't have thought so if he's using pneumatic switches, they'll just be 1way switches wired in parallel
I know I did my training a few years ago but I always thought staircase lighting was wired as an intermediate circuit, but things do change and if there is a newer better way to do them them then fair dos
When the OP said Pneumatic switches I sort of thought he meant something like these
https://www.sparksdirect.co.uk/ellipse-adjustable-time-delay-push-button-switch#.VW_xANKqqko
Which are intermediate switches
2way and intermediate switching is normal for houses etc but communal staircases have used time lag switches in parallel for far longer than I've been in the job.
That's not an intermediate switch, it's a 1 way switch, look at the connection diagram. An intermediate switch would have 4 terminals rather than the 2 which that one has.
Dave I'm not going to fall out over this. It is a domestic installation it is 3 story house as in the OP.
pneumatic switches are time lag switches.
The link to the switch I put up indicate that it can be used for intermediate circuits on the web page and the PDF
  • This kind of Time lag switches can be used in two way and intermediate switching arrangements without any extra wiring
  • Conventional Wiring Wire the units as in diagram 1. When using multiple switch positions
    see diagram 2.
    For two way and intermediate switching follow the diagrams overleaf.
    Note that as long as each switch position has a Live feed
    and a Live Out connection to the load then the switch will be
    properly wired.
They can and are used on an intermediate circuit. If you look on the 2nd page under the heading intermediate switching you will see a diagram showing a switch with the 4 terminals and then how to wire these switches
Actually look at the diagrams you are referring to, the time lag switches are wired in parallel in the 3way switch example with a diagram above showing a 2way and intermediate circuit. Each time lag switch only has live and sw live connections.
If they were intermediate switches then you'd have all sorts of problems with lights going off when I second switch is pressed during the time period, then defaulting to lights on instead of off etc
Reactions: 1 person
Help with diversity
Markymark981,
davesparks,