Hi all,new to this site need some advice on a fault, got an mcb type 2 30 amp which is tripping in an office on a ring final circuit on 1st floor, there are a 117 items of equipment plugged in but they are all low amperage things ie computers hard drives monitors etc. I have tested the circuit have continuity, insulation resistance is perfect , change breaker while its an old version and have PAt tested all item plugged in, tonight I have had a clamp meter on the circuit and its only pulling 15 amps, any idies what to do next? Please
 
Hi all,new to this site need some advice on a fault, got an mcb type 2 30 amp which is tripping in an office on a ring final circuit on 1st floor, there are a 117 items of equipment plugged in but they are all low amperage things ie computers hard drives monitors etc. I have tested the circuit have continuity, insulation resistance is perfect , change breaker while its an old version and have PAt tested all item plugged in, tonight I have had a clamp meter on the circuit and its only pulling 15 amps, any idies what to do next? Please

Install an BS3036 40 A FUSE mate will sort your issues
 
so i assume it was the old breaker that kept letting go?...
have you not thought that it might just be a bit tired?
 
117 items on an RFC drawing 15A, I wonder if he only clamped one leg of the ring...surely not?
An average of 30W per item, could that be right for an office?
 
Yes seems to only happen in morning maybe when cold! Tried replacing mcb. Don't think a bs3036 breaker will fit in that board it's the old mcb type 2 with the 4293 rcd
 
I have had a clamp meter on the circuit and its only pulling 15 amps, any idies what to do next? Please
Try another test with a clamp meter that measures true RMS. With 117 items of IT equipment I can give you very good odds the power factor is appalling and it's an overload fault.
 
Thanks marvo was getting a bit stuck to b honest. There are only about 16 twin sockets in the place there are extension leads off extension leads off extensions leads loaded with gear I no there all suitably fused bit is that safe?
 
Mainly happends first thing in morning why you say does it happen when it's cold?
What type of heating does the office have? Not unusual for office workers to whack on a few convector etc heaters to boost the temperature first thing of a morn (especially Mondays) - that could be your overload.

And, if they are using lots of trailing leads, tell the boss that he needs an extra circuit (or two)!