have you actually tested the circuit for continuity and meggared it to see if everything is alright? then taken a zs reading? just a thought haha
 
Heads up my @@@@!! Can someone help. Stil on job phone 07859819198 office stil tripping 5hrs overtime, new board ,rcbo,s and no hair left
 
High earth leakage? (thinking out loud).

Unplug EVERYTHING and IR the circuit at 500V.

If it tests 100% clear then there is an overload or short circuit.

Cant be anything else really.
 
Ha home finally ! Yep peeeee.. New circuit for each room 4 rooms 4 radials 6 computers on each hopefully problem solved let u no in morning if I get a phone call or not!
 
High earth leakage? (thinking out loud).

Unplug EVERYTHING and IR the circuit at 500V.

If it tests 100% clear then there is an overload or short circuit.

Cant be anything else really.
sod that....zap it at 1000V...if theres owt there....that`l find it...
 
Eeek, I get skittish even using the 250 range if there's IT equipment. Problem is even at 500v it's way over the clamping voltage of most surge arrestors so it might not give you a meaningful reading if the equipment is still in circuit. If all the equipment is unplugged then go wild with a 1kV test.
 
Eeek, I get skittish even using the 250 range if there's IT equipment. Problem is even at 500v it's way over the clamping voltage of most surge arrestors so it might not give you a meaningful reading if the equipment is still in circuit. If all the equipment is unplugged then go wild with a 1kV test.
my point at #23
 
Read the thread people already tried this a looooong time ago! Thanks for any replies anyway hopefully it's sorted,find out shortly..
 
upgrade CU with new breakers and RCD. In the meantime break the ring in make it a parallel circuit and see if it trips.
 