Just a quick one off my phone whilst still on the rounds...

been queried by a client I've done an eicr for...

she's got someone to act upon the c1,c2,c3 I dished out to her install......

there was was a socket off a spur wired in 1mm and whilst I'm aware that all power circuits must be a minimum of 1.5mm (table 52.3) I gave It a c3 because it's method c ( and a very short run)which can take 16a off 1mm.... So I fail too see the potential danger?

this little **** house been gobbing and told the client I'm clueless now before I smash his little brains In would you fellas of give it a c2 or c3 ?
 
Is this GLENNSPARKS you're talking about? :-)

C3 from me.

Hahaha, quite possibly - although i heard Glennsparks wires his rings/radials and spurs in 0.75 flex though :rofl:

I've spoke to the client again, and it sounds too me like the little swine has been trying to do extra work whilst he was there. Client wasn't interested in rectifiyng the C3 (most aren't lol) and he was pushing for it to be done, that's when he started saying it was a C2 and not a C3 and HAD to be done....must of been short of work, little ****.
 
get the gob****e to specify the regulation and explain why he considers it as a potential danger.
 