Just a quick one off my phone whilst still on the rounds...
been queried by a client I've done an eicr for...
she's got someone to act upon the c1,c2,c3 I dished out to her install......
there was was a socket off a spur wired in 1mm and whilst I'm aware that all power circuits must be a minimum of 1.5mm (table 52.3) I gave It a c3 because it's method c ( and a very short run)which can take 16a off 1mm.... So I fail too see the potential danger?
this little **** house been gobbing and told the client I'm clueless now before I smash his little brains In would you fellas of give it a c2 or c3 ?