Hi all,
Chapel, fire damage in switch room, every pew has an ancient tubular heater = 70+ heaters, none of them guarded, heard stories of melted shoes whilst praying!
Testing all cables prior to renewing switch gear as pre 1965 wiring. TN-C-S 2 phase supply...yes it is.... L1 and L3 only into building
Heaters connected 3/4/5 at a time on radials, no issues with overloading, each radial on 2.5mm, highest current being pulled 10A.
Tests going okay until low IR on earth to N, earth to live okay, between LN okay.....ahhhh old fused spurs..... so only single pole switch...but why on N....further checks.....all heaters record approximately 0.4Mohm on element to earth.......
Any ideas how I can explain in the morning that "yes they are working but....."?