Hi all,

Chapel, fire damage in switch room, every pew has an ancient tubular heater = 70+ heaters, none of them guarded, heard stories of melted shoes whilst praying!

Testing all cables prior to renewing switch gear as pre 1965 wiring. TN-C-S 2 phase supply...yes it is.... L1 and L3 only into building

Heaters connected 3/4/5 at a time on radials, no issues with overloading, each radial on 2.5mm, highest current being pulled 10A.

Tests going okay until low IR on earth to N, earth to live okay, between LN okay.....ahhhh old fused spurs..... so only single pole switch...but why on N....further checks.....all heaters record approximately 0.4Mohm on element to earth.......

Any ideas how I can explain in the morning that "yes they are working but....."?
 
Was the 0.4 Megs with all elements together or 0.4 megs per element? Maybe run them for a few minutes and re-test IR of elements.
 
Pretty sure regs ask for >2Mohms for wiring....so why would you suggest it's okay for an appliance as this would fail a PAT
 
Hi all,

Chapel, fire damage in switch room, every pew has an ancient tubular heater = 70+ heaters, none of them guarded, heard stories of melted shoes whilst praying!

Testing all cables prior to renewing switch gear as pre 1965 wiring. TN-C-S 2 phase supply...yes it is.... L1 and L3 only into building

Heaters connected 3/4/5 at a time on radials, no issues with overloading, each radial on 2.5mm, highest current being pulled 10A.

Tests going okay until low IR on earth to N, earth to live okay, between LN okay.....ahhhh old fused spurs..... so only single pole switch...but why on N....further checks.....all heaters record approximately 0.4Mohm on element to earth.......

Any ideas how I can explain in the morning that "yes they are working but....."?

If it's just the heater elements you've answered your own question there.
"Yes the heaters are working.....but.... a test has shown they are below the minimum required insulation resistance and ideally should be replaced"
 
The leakage current at 0.4 megs is just over 2mA. This is less than your average computer or anything else with a switch mode power supply. I'd be loathed to recommend replacements unless the regs leave you no option. Test them again when they're warm, I bet the insulation will be much higher.
 
My mistake just done a relook through my books

The applied test voltage should be approximately 500 Vdc


Class 1 heating equipment < 3kW 0.3M Ohms
Class 1 All other equipment 1M Ohms
Class 2 Equipment 2M Ohms

I think I'll recommend that the fuse spurs are changed to double pole so at least I can easily test the cabling
 
and just for completion

Earth leakage test:


Class 1 Handheld Appliances 0.75mA
Other Class 1 Appliances 3.5mA
Class 2 Appliances 0.25mA
 
That makes me a lot happier. It would be a great shame to rip out the existing heaters when they would probably outlast the new replacements by decades.

I'd run all the heaters together and use an earth leakage clamp around the live and neutral supply wiring simultaneously to get the actual leakage value. If it's substantial maybe suggest they go on their own RCBO's as a precaution.
 