Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a Ryefeid and one earth conductor so cannot think why this might be low on one phase only.One thing I did see was L1 fuse at Ryefeid was doubled up with another circuit (dont know what as no labelling). Voltage to earth for each phase at surge was normal. Wish I had carried out a loop to Neutral while I was there but did not. Anyhow it's a mystery; any thoughts?
 
Had this before, found by the DNO to be a corroded fuse carrier on a pole mounted fuse on their LV network
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Hi Zs on one phase only
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Eric12,
Last reply from
AH86Spark,
Replies
1
Views
852

Advert