Dear All
A mate of mine recently asked me to look at his installation. It has been wired to the 17th edition and all looks kosher, but when I carried out some testing I discovered that it had High impedance values. I disconnected the Main earth that had been connected to an earth clamp, attached to the armouring of the Supply Authority cable (old type armoured covered in hessian and bitumen). Took a reading from this clamp, this gave me a reading of 4.29 ohms taken with a Fluke 1653. The type of supply is TNS.
My questions are these:
1. Is it the responsibility of the Customer or the Supply authority to provide an Earth?
2. Is there a charge for the customer if they request a TNC-S supply (PME) instead of a TNS, seeing there is no Earth provided.

Kind Regards

Steve F
:rolleyes:
 
Thanks for your reply. The supply authority attended the property in question to-day. They said that the cable sheath was not and has never been connected to earth and that an electrode will have to be installed. I find this extremely hard to believe as this would mean that the property which was built in the 50's has never had an earth and has always been a TT system. I think I will have a look at his neighbours house.

Is there a certain distance the Earth Electrode has to be away from the property?
 
Normally somewhere sensible just outside the location of the CU.

Sounds to me like the property was earthed through the incoming gas and/or water service pipes.

Not ideal!!!
 
Yes your probably right!
When you say just outside the location of the CU, do you mean outside the property as the CU is under the stairs.

Regards

Steve F
 
yes it needs to be outside the house just find the most convenient route out and run that way, it doesnt need to be the shortest way, i would put the stake in an earth pit of some sort to protect the connection.
 

Reply to High Earth Loop Impedance in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
478
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
  • Article
Electrical2Go - Megger MFT Deals! Upgrade your toolkit with our exclusive offer! Purchase any of the Megger advanced multifunction testers –...
Replies
0
Views
558
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K
Hi A customer has a new farm shed going up supplied also from a new 100KVA transformer right outside. The supply spec states that PSCF could be...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock