supasparxs
being from an IT background, heard of wi-fi ? lol
haven't you heard that a wired link is more reliable than a wireless one?
(I've just spent a couple of days sorting the new virgin wireless hub)
being from an IT background, heard of wi-fi ? lol
Changing the aspect slightly (away from WiFi that is)
have you considered offering RCBO's rather than a split load RCD board?
I have used CPN boards a few times and the RCBO's come in at about £14 each
this means that you can offer a fully-loaded RCBO board for about the £90 +vat
This is certainly the way i like to go if the finances make sense usually, like you say RCBO's can be picked up at such a good price nowadays it seems a little backwards not to go that option.
You could give a price option for RCD split board or the more expensive option for RCBO's (don't forget there is more testing with a fully loaded RCBO board). PM me if you want the details of my wholesaler who stock it
You will be lucky to get £2200 around my way, its crazy. I had some experience working with two niceic sparks, 3 bed, full rewire, two 10 hour shifts over a weekend, left plastering for custy to sort though.
Over a weekend!!!
Cash in hand???????
Don't forget that 'building regs' state that 3 out of every 4 lights must be energy efficient
Yes mate, cash in hand, all above board though as was certified and notification to NAPIT so the guys i was working with would still have to declare it.
It just seems there are some crazy prices out there at the moment, the two guys that have been giving me some experience days with them work full time for medium size sparky firm round my way but work together on their own private stuff evenings and weekends so can price like this coz its still good money for two days work. Doesnt help the trade though for the self employed guys trying to quote against them.
Well check out 3.6.1 In the on site guide on P(21-22)...for TT systems ALL circuits must be given RCD protection mate and the only way to get discrimination would be tu use an s type ...upstream of the outbuilding feed.....which would then feed another RCD at the outbuilding end............Why if there was an outbuilding??