The circuit supplying the SPD within the DB I wouldn't really class as a general use circuit such as a final or distribution. It is contained within the enclosure with very limited risk of damage or failure causing a fault that will allow the enclosure to become live. If a homeowner does manage to drill through the cable putting up a shelf then they really need to step away from the tools.
Double check with the manufacturers but a lot of the tails connecting to the SPD will be double insulated. Some manufacturers are happy for the DNO fuse to provide protection if below a certain rating, IIRC Wylex is 100 amps but it's been a couple of years since I looked at their kit.
SPDs do not use current so terminations should remain as installed over time, no movement due to thermic cycling etc. If installed correctly should be fine to provide many years of service. They're designed to work once and the installation should have a full I&T after surge event to identify any issues that have arisen.
If a full RCBO board is installed and the manufacturers state their RCBOs are suitable for use on a TT system if backed up by a double pole main switch and the incoming tails are supported by a suitable means then why the need for a time delayed main switch?
Double check with the manufacturers but a lot of the tails connecting to the SPD will be double insulated. Some manufacturers are happy for the DNO fuse to provide protection if below a certain rating, IIRC Wylex is 100 amps but it's been a couple of years since I looked at their kit.
SPDs do not use current so terminations should remain as installed over time, no movement due to thermic cycling etc. If installed correctly should be fine to provide many years of service. They're designed to work once and the installation should have a full I&T after surge event to identify any issues that have arisen.
If a full RCBO board is installed and the manufacturers state their RCBOs are suitable for use on a TT system if backed up by a double pole main switch and the incoming tails are supported by a suitable means then why the need for a time delayed main switch?