I'm doing a job this week wiring up some site cabins on a dockyard, I'm running a 10mm two core SWA 50 metres, there is a 9m section which is exposed to vehicles, one of them being a truck which emptys the portaloo .im thinking if protecting the cable with some sort of protection but was wondering what type of weight it would take?, cheers
 
highways grade rubber channel protectors will take 40t HGV no prob ;-)
---- knows where you can get the stuff lol.
 
Doesn't seem to be a good idea running trucks over a wired armoured cable,the chances are the cable will flatten quite easily

Nip it through some conduit



I wonder what the score was in the rugby yesterday lol
 
Last edited:
Your in a dockyard so getting some angle iron to cover it should be no problem



I wonder what the score was in the rugby yesterday lol


 
Last edited:
We use class 50mm class 10 HDPE irrigation pipe as ducting buried at 500mm or deeper. It's very inexpensive and easily obtainable, also resilient even to trucks if it isn't buried too shallow. It comes as a roll and is easy to install.
 
Hard to explain the job area!,the only vehicle that will go near it is the truck , every two weeks, whole job being decommissioned in 9 months, I might just get the proper protectors and try and adapt them some how , that said I can't seethe conductors being damaged when protected by armour and steel conduit
 
He is in a Dock yard, they have scaffold coming out there ears,it will take the weight of a tracked mobile crane; Doing doghnuts on it. well not exactly Ken Block driving.
 