How to do Ze ie two lead high test using the Robin kts 1620 instruction, not sure what settings to use ie 20 ohms 200 ohms or 2000 ohms and for the psc ie 200a 2000A or 20KA any help is much appreciated
 
Maybe no one has used that model? Presumably you don't have the instruction book now?

Recent MFT auto-range so you just connect up, double-check no one is doing anything to the electrics elsewhere, and press the test button.

As a rule any TN-S or TN-C-S is going to be less than 20 ohms if in good condition so you could assume that, where as TT you might start on 2k and then go down to 200 ohms if (as it should be) the rod is below 200 ohms.

I don't know if that model has any safety features to stop > 50V on the earth under test, so starting high R and dropping down ought to keep the volts to a level that is safe.
 
Maybe no one has used that model? Presumably you don't have the instruction book now?

Recent MFT auto-range so you just connect up, double-check no one is doing anything to the electrics elsewhere, and press the test button.

As a rule any TN-S or TN-C-S is going to be less than 20 ohms if in good condition so you could assume that, where as TT you might start on 2k and then go down to 200 ohms if (as it should be) the rod is below 200 ohms.

I don't know if that model has any safety features to stop > 50V on the earth under test, so starting high R and dropping down ought to keep the volts to a level that is safe.
Thank you
The Robin kts 1620 has two sets of Leeds one is for testing at the socket and one is for testing at the consumer unit this set is a three lead one red probe one black with crocadial clip and one green with crocadial clip book says nothing about external loop impedance testing just zs
 
book says nothing about external loop impedance testing just zs
Measuring Ze is exactly the same as Zs, except you need to have the supply to all circuits off and have isolated the incoming earth to test to it.

Normally Zs is slightly lower than Ze due to parallel paths to Earth from bonding to water, gas, etc. It can be significantly lower if you are in a block of flats, etc, so all of the extraneous pipes are also well-bonded to the supply earth and are not just relying on metal in ground.
 
Been using Robin for years, not that model but they normally need three leads.
Thank you for your help
So do we need to do Ze test I keep hearing about doing the external earth loop impedance as two lead high ie remove the main 16mm earth from the cu connect one leed with crocadial clip to that and with the red lead probe on to the incoming line
 
You really should check Ze as Zs can magically become higher in the future when someone changes a service pipe to plastic and those parallel paths are largely gone! Much more so on TT when the rod might be rubbish and so far the installation has really been relying on the water pipe, etc.

Some MFT will do two-lead tests, other demand all 3 are connected. If accessing the supply N when isolated for a 3-lead test is difficult then put N & E together to the supply CPC and then the probe to L for the test.
 
You really should check Ze as Zs can magically become higher in the future when someone changes a service pipe to plastic and those parallel paths are largely gone! Much more so on TT when the rod might be rubbish and so far the installation has really been relying on the water pipe, etc.

Some MFT will do two-lead tests, other demand all 3 are connected. If accessing the supply N when isolated for a 3-lead test is difficult then put N & E together to the supply CPC and then the probe to L for the test.
Thank you that's a big help
 
When doing a psc test using the Robin kts 1620 MFT what do you set the PSC dial to 200A 2000A or 20KA? or should I start with 20KA and then work down the scale? TNC-S SYSTEM
Start on the lowest 200A range, and if it is over that go up.

That way if it lacks any safety features to limit the earth rise during test you keep it to a minimum.
 
So when you are doing a Ze or Zs the expected ranges are <0.8 ohms or <0.35 ohms unless testing a TT system. So it is a low range test. You are not actually testing the PFC, you calculate that from the measurement found on doing the above tests.
 
Just looked at the model. It is obsolete by the looks of it. I see it actually does a PSC test, which means it will measure the Zs and calculate the PFC for you. I would use the loop test and calculate personally. Is your model actually calibrated?
 
Yes it is calibrated
And it may be 20 year's old but it still complyant as the regs clearly states ANY test instrument that can perform the tests will be complyant with BS 7671 it does NOT mention any brand names or age of the instrument, also many many electritions still use them, and faver them over the over priced big brand names
 

Reply to How to do Ze test in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
Replies
5
Views
326
How to do Ze test using the Robin kts 1620 instruction, not sure what settings to use ie 20 ohms 200 ohms or 2000 ohms and for the psc ie 200a...
Replies
3
Views
2K
Hello, I have an all-in-one washer/dryer unit and it is giving me error codes. I have the manual that describes how to test the various...
Replies
2
Views
535
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock