ianphilip007

hi guys

have a customer who has bought a humidistat/timer fan which has a SL Perm L and N connections. He has stated that he wants the fan to only operate due to humidity but not to be activated by the light switch.

The existing fan has a Live/Neutral & Earth via a 3amp FSU. I was wondering if i only connect to the perment live and Neutral will the fan just operate on the humidistat or will it not work at all without a switched live.

many thanks
 
you might need to link the L and S/L in the fan. bit of trial and error, or...... follow manufacturers instructions.
 
hoping it will work, agree will have to try some trial and error or find a humidistat fan that does not require a switched live.
 
Call the technical line at the manufacturer

or get the stupid customer to take it back and get a humidstat only unit!
 
Last edited by a moderator:
hi guys

have a customer who has bought a humidistat/timer fan which has a SL Perm L and N connections. He has stated that he wants the fan to only operate due to humidity but not to be activated by the light switch.

The existing fan has a Live/Neutral & Earth via a 3amp FSU. I was wondering if i only connect to the perment live and Neutral will the fan just operate on the humidistat or will it not work at all without a switched live.

many thanks
Don't take this the wrong way Please, but have you read the instruction leaflet which comes with the fan and it usually has a wiring diagram on it???
 
yes it indicates perm live, switch live, and neutral, required at terminal block., but he doesnt want it to operate when the light is switched on. cant find a non timer humidistat fan so i think a humidistat and pull cord is the best option. if it wont work without a switched live inpiut
 
All the one's I've ever fitted you just ignore the S/L - it basically just parallel switches with the internal sensor.
 
the answer to the question is almost certainly yes, just stick the humidistat in the circuit from the permanent live to the fan, sorted.

you'll need to test the humidistat settings though, they can usually be adjusted, so make sure it comes on before it gets too steamy.

but yes, check the instructions.
 
thanks gavin and all, it should work just on the humidistat with a perm live and neutral as the switched live is basically to trigger the overun timer in this type of fan i beleive, which is not really a requirement of the customer.

only way to find out is give it a try thanks for your input.
 