I've recently got into Inspection and Testing after being on install work for several years and have a few questions regarding several grey areas:
1. How do you properly carry out IR testing of individual circuits within installations that consist of single insulated cables (usually older buildings) where the cpc and neutral conductors are most likely in the incorrect numbered terminal of their respective bars?
2. On premises where a back up generator is present what exactly has to be entered in the additional page of a periodic certificate in terms of earthing? (i use Amtech) ie: as it is generator should this always be a TT or would it be the same as the earthing system present within the main installation?
3. On installations where metallic conduit and trunking has been utilised for the cpc's is it easier to carry out R2 testing of circuits using the long lead method as opposed to R1+R2 testing?
4. Should i generally note MCCB's as overrated if they are set to a satisfactory rating but could easily be increased so as to become too high for the cable connected.

I do have a few more questions regarding I+T but I thought I would start off with the areas I wanted clearing up as soon as possible.


Thanks
 
A weeks inspecting and testing course, such as 2394/5 would be suitable for you, as your queries are quite basic, and should be the sort of things that you should know before doing any inspecting.

Remember, it is you who signs the Condition Report, and if you don't know how to test R1+R2 properly, then how can you be sure that the rest is being done correctly? A slight mistake, through lack of experience/knowledge can have big consequences, so I'd recommend you getting some more training before embarking on I&T for a living.
 
Actually fair questions - training courses don't cover everything. With lots of singles in a board I usually leave them til last, then by process of elimination work out which cable is for which piece of equipment, there are various ways but if you have the board to yourself and can knock the whole lot off its much quicker and easier. Not clear on the issue of the generator, by inspection you need to determine the type of earthing used. Trunking, anyway you like as long as the R1+R2 is what is experienced at the equipment side, you could use a crock jumper, multiple paths is the most difficult to determine like steelwork and piping but TBC I don't fret over this as long as its in good condition is supported well and gives good readings. MCCBs sometimes I do see them set to max over the cable rating, I generally get agreement to reset them to the appropriate level and move on.
 
To be honest I think they're pretty fair questions. I have the 2391 qualification and, of the 4 questions, 3 of those definitely wouldn't have been covered in the course, unless the student had specifically asked. Especially the questions about the generator and the MCCB's. Like plugsandsparks stated not all areas are covered, it's usually just a standard agenda that doesn't really skew off course and take into account general snags and solutions. I've also done loads of R1+R2 testing but I was asking simply if the long lead R2 test is more commonly practiced in installations with large amounts of metalwork. In regards to the questions I have found that you find MCCB's quite commonly where the In setting has been set to too high a value to safely protect the cable. I've also found in old distribution boards in factories/workshops etc that it can be very difficult to determine which neutral and cpc conductors match up to their respective line conductors when the board is full, has had lots of additions/alterations and is exclusively PVC single cables as opposed to multicore cables, which are obviously easier to identify.
 