Whilst awaiting my niceic assessment i have been to price up a job, basically it is a loft conversion and i was planning to put a seperate cu up there as the route is awkward.
It needs smoke detectors on each floor,a ring main and lights.
2 bedrooms and one bathroom .
i have been out of domestic for a couple of years so think my ideas are good just thought i would run it past some people in the know!
The existing installation has a db with 1 spare way, it is protected with a 30ma rcd. i plan to put a seperate four way cu in the cupbaord in one of the bedrooms and take local circuits back to it. Was thinking a 6mm t&e from downstairs protected by 40A mcb total length around 8 metres. Cu would just have isolator as protected by 30a mcb. Am i supposed to fit a 17th edition db at the downstairs now or is the way i have suggested ok?
thanks
 
good point, i think i will price that in as it will be clipped direct but may pass through a cavity wall and not sure if there will be insulation in it or not.
thanks
matt
 
future proof it use 16mm ready for 10.5 kw shower and 3kw fan heater for the sake of 10 to15 quid
 