Discuss identifying systems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

M

malawi

hi guys i have asked a similar question last week regarding identifying tns or tnc-s systems if not clearly visible .i have 2392 and hopefully would like to pass 2391 in future so have practising on my brothers high rise flat .when i asked before i was kindly told to do pefc and pscc tests and if same it was tnc-s .i done both tests and got PEFC 1.64KA and PSCC 1.99KA .how close do these readings need to be to identify TNS or TNC-S any help would be greatly appreciated thanks in advance
 
What was your Ze reading that would help in deciding or as a last resort ring your DNO as they have that information.


Hope that helps


Chris
 
hi guys i have asked a similar question last week regarding identifying tns or tnc-s systems if not clearly visible .i have 2392 and hopefully would like to pass 2391 in future so have practising on my brothers high rise flat .when i asked before i was kindly told to do pefc and pscc tests and if same it was tnc-s .i done both tests and got PEFC 1.64KA and PSCC 1.99KA .how close do these readings need to be to identify TNS or TNC-S any help would be greatly appreciated thanks in advance

Doing PEFC and PSCC tests can be misleading as all bonding will be in place giving parallel earth paths.

Try doing the same tests with the installation isolated and bonding disconnected. If TNC-S the readings will be the same.
 
That would suggest TNCS as max on that is 0.35 TNS is 0.8 and I would think if you followed the above advice your short circuit and fault readings would be the same.

Hope that helps


Chris
 
That would suggest TNCS as max on that is 0.35 TNS is 0.8 and I would think if you followed the above advice your short circuit and fault readings would be the same.

Hope that helps


Chris

Not necessarily. My sister's TNS supply has a Ze of 0.09Ω :D
 
Last edited by a moderator:

Reply to identifying systems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
997
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Replies
22
Views
3K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
718
  • Article
Electrical2Go - Home Security: Using Floodlights, CCTV, and Door Entry Systems In an era where technology is advancing rapidly, home security has...
Replies
0
Views
303
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock