The recent click-bait thread on radial vs ring final circuit descended in to the usual arguments ranging from sane to near-religious, but one issue that was raised among the general noise is the risk of a ring with an open somewhere.

So I wondered if the folk on here that do many EICR and similar work could comment on the following:
  • Roughly what percentage of tested RFC do you see with an open ring?
  • Is there any more common fault than other (e.g. is E more likely to be open than L, etc)?
  • How often are those incomplete rings showing any sign of thermal stress / overheating?
And please folks keep the thread discussion on this one point of open rings, not the general merits of RFC vs Radial, etc.

TL;DR Open ring, any common cause and does it overheat?
 
Aico 3000
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
C

ChrisElectrical88

-
Mentor
Esteemed
Arms
Id say of all the circuits I test 2% have an open ring so about 1 in 50.
I’d say 20% have a off reading so line and neutral not the same or CPC >1.67 that of the line and neutral.

Ive not commented on the other thread, cause it’s just daft. Both circuits have their uses. I actually wired a 32A 4mm ring last week, it’s the first time it’s been practical to do so with a fully clipped direct run.
 
R

radiohead

Esteemed
Arms
I think a 'survey' on open rings will inevitably depend on the type of properties people are testing. I find a lot of broken rings in 60's-70's houses with original and invariably altered wiring, and recently attended a fault where no less than 3 outlets had burnt out/damaged line terminations, the cause being a combination of loose terminations and increased load due to a break in r1. I would suggest a high percentage of such properties have RFC faults. I suspect those who test mainly commercial or industrial find far fewer broken rings
 
P

pc1966

Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #4
Id say of all the circuits I test 2% have an open ring so about 1 in 50.
I’d say 20% have a off reading so line and neutral not the same or CPC >1.67 that of the line and neutral.
That is interesting, as that is picking up bad connections as far more of an issue than complete opens.

Ive not commented on the other thread, cause it’s just daft. Both circuits have their uses. I actually wired a 32A 4mm ring last week, it’s the first time it’s been practical to do so with a fully clipped direct run.
Exactly!

Oddly enough my current work has a 32A RFC of 12 double sockets in 4mm simply because most other circuits need 4mm, so no point in buying some 2.5mm as well.

It also has 6 outdoor sockets for occasional maintenance use as two radials, also in 4mm for voltage drop reasons, but on a 20A MCB due to the rating of the isolator switch.
 
Dannyboybl00

Dannyboybl00

-
Over the past year I reckon 20% of the EICRs I've done (around 50) have revealed an open ring. All but two have involved neutral and CPCs with the breaks being due to poor connections at a socket (or weak CPCs snapping in a backbox). Not seen any thermal damage as yet.
 
P

pc1966

Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #6
I would suggest a high percentage of such properties have RFC faults. I suspect those who test mainly commercial or industrial find far fewer broken rings
I suspect many properties of the 60s/70s coming up for sale now as old folk die or move in to retirement homes will have had no EICR at all, and a lot of dubious changes to make up for a lack of adequate provision of sockets by today's standards.

But as you say industrial and commercial tend to have more professional modifications and inspection/maintenance over the years.
 
C

ChrisElectrical88

-
Mentor
Esteemed
Arms
That is interesting, as that is picking up bad connections as far more of an issue than complete opens.


Exactly!

Oddly enough my current work has a 32A RFC of 12 double sockets in 4mm simply because most other circuits need 4mm, so no point in buying some 2.5mm as well.

It also has 6 outdoor sockets for occasional maintenance use as two radials, also in 4mm for voltage drop reasons, but on a 20A MCB due to the rating of the isolator switch.
Yes there are defiantly a lot more poor connections than open rings. I mainly test social housing which are maintained, erm I’ll say ‘averagely’ well. So the lads doing to works should be competent enough.
I do like the idea of 32A 4mm radials everywhere, however it doesn’t take much to de rate 4mm below a 32A current carrying capacity.
Post automatically merged:

I should add that I did 2 years solid of testing Pubs a few years ago and in that environment getting a good ring was about 50/50 chance.
 
P

pc1966

Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #8
Certainly I suspect that bad connections are more likely to be a source of thermal damage than simply the loss of one of the live conductors' continuity.

That is an issue for both RFC & radial, though we have AFDD to save the day.

Stop laughing at the back, you with the torque screwdriver!
Post automatically merged:

I should add that I did 2 years solid of testing Pubs a few years ago and in that environment getting a good ring was about 50/50 chance.
How odd, I would have expected them to be much the same as other commercial/industrial properties. Maybe those wanting to be pub landlords know more dodgy Dave DIYers to get work done?
 
C

ChrisElectrical88

-
Mentor
Esteemed
Arms
How odd, I would have expected them to be much the same as other commercial/industrial properties. Maybe those wanting to be pub landlords know more dodgy Dave DIYers to get work done?
Pubs are a different breed altogether. We would do a 20% test of the installation each year. In most cases I was getting the last 20% so all the rings were left as the years before the lads had just opted for the easier radials. Lots of adapted circuits, countless spurs on spurs. Pubs are awful. Still it’s rare I’ve seen any thermal damage on a ring.
 
Taylortwocities

Taylortwocities

-
Esteemed
Arms
Maybe those wanting to be pub landlords know more dodgy Dave DIYers to get work done?
I do work for a local landlord. He’s a tenant and is supposed to use the maintenance team from the brewery for jobs. But the maintenance team are
1. Crap
2. Come from the brewery 200 miles away. The landlord gets charged for time which includes travelling, so it’s expensive.
in my case I’m a trusted cheaper supplier for him and I get served first at the bar when it’s busy!
 
D

Dustydazzler

-
Esteemed
Arms
It’s fairly common to find an open rings or a big spur ring where it was a ring and someone has added multiple Extra sockets off a single spurred cable So you have multiple sockets on a single 2,5 cable

from what I have seen on youtuber electricians most of then now just swap out the 32a mcb for a 20a mcb rather than try to put all the sockets back on a complete ring

but that imo is a bit lazy and you are reducing The Ccc of the circuit which Could have originally be designed to supply the whole house worth of sockets on a 32a ring circuit
 
P

pc1966

Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #12
That is a simple and cheap "fix" as you say, but not very elegant or professional.

Still, if the usual suspects from the kitchen (washing machine, dishwasher, etc) are on a different circuit I doubt most houses would draw 20A for the remaining sockets (unless they rely on a lot of plug-in electrical heaters, of course).
 
Get paid faster with card payments | Go Paper Free - Save Hours | Offer Finance to Customers
This official sponsor may provide discounts for members

Reply to Incomplete ring circuits? in the Electrical Forum area at ElectriciansForums.net

CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Top Bottom