One sure way to test if it is ghost voltage
is to test again with a low impedance anologue style volt meter.
that voltage will either be significantly reduced or gone altogether.
This is why some electricians have both a digital and anologue multi-meters.
:)
 
Should I be worried, or is it just one of those things?
Hi,Imagine you are setting up,to measure the speed of a bird,flying past,in a corridor you are stood in.
A bird flies past in another,adjacent corridor,and your bird-speed-indicator,picks up the draft from its wings,and records it. This is what you have measured.

To separate your bird,from any other flying objects,all the doors must be closed in your corridor. This is achieved by using a measuring device which applies a load.

...and don't forget to put a GS38 rubber cap,over any sharp beaks,whilst measuring ;)
 
Hi,Imagine you are setting up,to measure the speed of a bird,flying past,in a corridor you are stood in.
A bird flies past in another,adjacent corridor,and your bird-speed-indicator,picks up the draft from its wings,and records it. This is what you have measured.

To separate your bird,from any other flying objects,all the doors must be closed in your corridor. This is achieved by using a measuring device which applies a load.

...and don't forget to put a GS38 rubber cap,over any sharp beaks,whilst measuring ;)




So PEG what I think you may be saying is Micheal should stop flapping
 
i'd give him the bird.
170px-The_finger.jpg
 
This is due to unbalanced of three phases and a current flowing down the Neutral. That current times the conductor resistance equal the voltage you found, not unusual especial on rural over head line net works where different houses are fed from one of the phases and two are loaded and the third is not.
 