Good Evening Guys,
In line with our local DNO's rules.
When advising domestic clients the guidelines for the civil side of underground cable runs (which we never perform) I always explain that the cable should be burried at a depth of 600mm under roadways and 450mm under footways, the cable should be run within a 38mm black duct with the words electrical cable printed on its surface and an electrical cable tape should be installed 100mm directly above the ducting/cable run.
As I have stated this is the instruction that I always pass across to clients as I see it as good practice so I have two questions to post for debate.
1. Where would we stand if the client cuts corners and does not install as per our instruction thus leading to problems at a later date.
2. Is this the way you guys would suggest to clients to install or am I going overboard?
Regards SYKRAPS.
In line with our local DNO's rules.
When advising domestic clients the guidelines for the civil side of underground cable runs (which we never perform) I always explain that the cable should be burried at a depth of 600mm under roadways and 450mm under footways, the cable should be run within a 38mm black duct with the words electrical cable printed on its surface and an electrical cable tape should be installed 100mm directly above the ducting/cable run.