R rmaynard Mar 28, 2012 #1 can these be on a ring main circuit or do they have to be supplied independantly?
R rmaynard Mar 28, 2012 #3 3 I think, iv not seen them yet --- I am here: http://tapatalk.com/map.php?xvk4yz
G gnselectricals Mar 28, 2012 #4 I had one last week which was 9.5kw , tiny little thing, could hardly get a 4mm flex into it Sent from my iPhone using Tapatalk
I had one last week which was 9.5kw , tiny little thing, could hardly get a 4mm flex into it Sent from my iPhone using Tapatalk
M mhar ~ Arms Mar 28, 2012 #8 Over 3kW on a separate circuit or do you mean a ring with a number of these on it?
telectrix ~ Mentor Arms Mar 28, 2012 #10 so, 3 @ 3kw each =40A. have to be a 4mm RFC on a 50A MCB. assuming derating factors don't rule 4mm out. Last edited: Mar 28, 2012
so, 3 @ 3kw each =40A. have to be a 4mm RFC on a 50A MCB. assuming derating factors don't rule 4mm out.
S Silly Sausage Mar 28, 2012 #11 rmaynard said: sorry yes hand washer. it would be a ring with 3 on Click to expand... Is this some kind of washroom or the like? With diversity (see App 1 OSG) you're looking @ 30A. I think I'd put them on their own Radial.
rmaynard said: sorry yes hand washer. it would be a ring with 3 on Click to expand... Is this some kind of washroom or the like? With diversity (see App 1 OSG) you're looking @ 30A. I think I'd put them on their own Radial.