GLENNSPARK
yep....and i`ll certainly go up to 1KV if i suspect it needs it...There are plenty of 1KV IR testers out there that have a 1000 megohm range. No problem at all, shoving 1KV up a domestic circuit. ..lol!!
yep....and i`ll certainly go up to 1KV if i suspect it needs it...There are plenty of 1KV IR testers out there that have a 1000 megohm range. No problem at all, shoving 1KV up a domestic circuit. ..lol!!
I'm surprised. Small circuits on dry days that's fair enough, but large stuff and most anything when it's really humid you cannot always get up to hundreds of megs. With humidity, it's not so much the cable but the creepage across the accessories, i.e. the insulation itself is OK but it's being shunted by conductive moisture paths. The more of these you have in parallel the more likely the reading is to fall below the range limit on your tester.just hadn't come across this before. Any time I've done it it's been >299 on new wiring.
Quite common - usually a combination of dielectric absorption in the insulation and driving off the moisture at the terminations. It's fun watching it climb towards the range limit but for normal work serves little purpose.The other thing I noticed was if I held the lead on, very slowly the value started increasing sometimes going the full way to >299. This just my tester, leads or what?
Lucien....come on.....you cant proffer statements like this one .....I'm surprised. Small circuits on dry days that's fair enough, but large stuff and most anything when it's really humid you cannot always get up to hundreds of megs. With humidity, it's not so much the cable but the creepage across the accessories, i.e. the insulation itself is OK but it's being shunted by conductive moisture paths. The more of these you have in parallel the more likely the reading is to fall below the range limit on your tester.
Quite common - usually a combination of dielectric absorption in the insulation and driving off the moisture at the terminations. It's fun watching it climb towards the range limit but for normal work serves little purpose.
Lucien
hmm....glenn, he did not say parallel paths as such, just that the more sockets you have ( which are in effect, in parallel across the circuit, ) each with some moisture involved, will reduce the reading accordingly.the more sockets, the more the leakage.
My 1000V Megger only goes to 999MΏ.
The Megger I had at work went in to 100’s of TΏ. Rotten sods wouldn’t let me take it with me when I retired. All the other test gear I was allowed to take but not that!
I wonder how many know the 1/10,000[SUP]th[/SUP] FLC calculations for IR readings. A must with old / large systems.