With a reading of 1.04 on both lighting circuits, What would be a feasible interval for the next inspection?

​

I think I would be making sure that there was not a smoke alarm on each circuit, or a dimmer switch that you have not disconnected for testing. I mean it's a bit of a co-incidence that BOTH circuits have broken down from many hundreds of Mohms when they were installed to exactly the same point of breakdown...

Which measurement is this BTW
L-N, LE or NE?
 
Last edited by a moderator:
Overall tested .609, Tested each individual circuit and get the following

1 L-L 50.7 L-CPC 34.5
2 L-L 30.2 L-CPC 4.14
3 L-L 56.3 L-CPC 15.73
4 L-L 5.75 L-CPC 1.04
5 L-L 4.84 L-CPC 1.08
 
Hi that reading was for Live - CPC, Prior to doing the test I did L&N - CPC
They wernt exactly the same, Near enough tho. But I understand its pretty remarkable that they are similar values
 
I would recommend a routine check in 1 years time. Which is in GN3 Table 3.2 Recommended initial frequencies of inspection of electrical installation.
 
I would recommend finding the fault. 1.04 is (and excuse the phrase here) Barely Legal!!!
 
I have got one today with a 0.71 on NE - I am going back to find out what is causing it. I am not pushing for a rewire. May be I am missing a trick?
 
Hi is there any signs of damp/moisture at all? And have you checked that no other electronic sensitive equipment is connected or hidden.
 