If I go with the belling, then it does state in the instruction book (just downloaded a copy to see ) 45 Amp breaker,10mm cable to the control unit, and 6mm from the control unit to the applianceWhat's the load of this new cooker
Geordie, i have noticed as time marches on, things that dangle unsupported tend to sag.

My question same as last 2, why are you changing to 10mm unless your cooker is over 8.5kW?
i have never had a cooker require a 10mm cable (except a commercial/industrial cooker!)
Which is where duct tape becomes useful. :rofl:

as i've already said. 6.0mm on a 32A MCB will handle any domestic cooker. anybody heard of diversity?