Guitarist
I think that this is a good case of "things change". Most cookers will be quite happy on the 6mm/32a combo, yet with ranges becoming more and more popular it's time to take each situation on its own merit now.
davethsparky;814715It did indeed run draw the full 50A when it's self cleaning cycle started up.[/QUOTE said:Those self-cleaning cycles tend to stuff up diversity calculations a bit...
If I go with the belling, then it does state in the instruction book (just downloaded a copy to see ) 45 Amp breaker,10mm cable to the control unit, and 6mm from the control unit to the appliance
It's easy to quote what we all think, but if any electrician ran a 6mm in with a 32a MCB, then the unit tripped when the range went into self-cleaning, who's going to have to put things right FOC? The electrician of course. If the manufacturers quote 10mm on 40/50A, then just do it.
Been mentioned on another thread, but I installed a new "range" style cooker the udda day with induction hobs, and an oven that could have both grill, and the oven, on at t'same time, like. Couldn't quite believe it myself as never seen that, but it was a very expensive oven (retail £5.5k, ex display she got it for £3k), and the function that allowed this space/time anomaly was .............
pizza setting!
it came with (also a first) the cable fitted to the cooker, it was 10mm2 3 core high temperature flex. Thought it was a water pipe at first.