Would this be acceptable as a maintenance free joint for 6mm T&E ? Stagger the joint. Solder the cables, heat shrink each joint and then heatshrink again over the top of both. No chance of it coming loose and would have double insulation with the individual and then combined heatshrink. It'll be a joint with no access at all once it's done. I really don't trust Wagos!
 
Would this be acceptable as a maintenance free joint for 6mm T&E ? Stagger the joint. Solder the cables, heat shrink each joint and then heatshrink again over the top of both. No chance of it coming loose and would have double insulation with the individual and then combined heatshrink. It'll be a joint with no access at all once it's done. I really don't trust Wagos!
Instead of soldered joints, BS 7671 standards encourage the use of modern, purpose-built accessories that create secure, maintenance-free connections. Options include:

Push-fit connectors (e.g., Wago terminals)
Crimp connections using appropriate crimping tools and terminals
Screw terminals within junction boxes or accessories
 
Instead of soldered joints, BS 7671 standards encourage the use of modern, purpose-built accessories that create secure, maintenance-free connections. Options include:

Push-fit connectors (e.g., Wago terminals)
Crimp connections using appropriate crimping tools and terminals
Screw terminals within junction boxes or accessories
Does it actually quote that?
 
I'm still not a lover of Wagos long term on 6mm or bigger where they can't be accessed. I would still prefer a known good solid solder joint.
 
Would this be acceptable as a maintenance free joint for 6mm T&E ? Stagger the joint. Solder the cables, heat shrink each joint and then heatshrink again over the top of both. No chance of it coming loose and would have double insulation with the individual and then combined heatshrink. It'll be a joint with no access at all once it's done. I really don't trust Wagos!

See Reg 526.2

I don't think the above meets the requirements.

Maintenance free junction boxes have cable restraints to prevent creep.
 