I've tried to understand one way or another but this seems to be connected to the DNO fuse/cutout, and then loops down (out of sight) and comes back up to connect to the outer sheath.
IMG_20231004_191431.jpg


The bonding looks like 6mm^2. And the connection point looks like that's the max it will take. As I understand it, TN-C-S needs 10mm^2 so TN-S?
 
It's impossible to tell from looking at it.

It would have originally been TNS and the original cutout has been replaced with that one.
But those cutouts have a removable N-E link, so it could still be TNS if the link has been removed or it may have been left in place to convert it to TNCS.
 
Thanks, though not the answer i wanted :(

I had a man out to change the meter, should have asked him. If the DNO fuse was 1/4" to the right, he could have changed it. Got to sort out the door for clearance.

There are two issues here. First I need another bond to the gas. From the CU? Or split the CU wire and a terminal block for the additional gas bond. Then we have the size issue. My house is in the process of being renovated, so now would be a good time to pull a wire.

It's an Earth Loop Impedance Tester that'll allow me to measure and find out? Ze reading or or something can be used to work out what I have.

I want to update the CU to 18th with RCBOs at some point so hoped I could sort bonding first.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Mars
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
Computer Science Bsc

Thread Information

Title
Is this TN-C-S or TN-C, also earth bonding size.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
mR__Slug,
Last reply from
mR__Slug,
Replies
2
Views
1,503

Advert