Hello everyone, first post here. I can really find a definitive answer to this question so thought I'd ask here.
I've drawn 2 wiring diagrams showing a single phase supply, I'm wondering which one of these would be the best/most suitable instal method?
I have a few notes to point me in the right direction but I want a definitive answer.

  • Part 2 Definitions: “Neutral conductor” is a live conductor. Why it matters: Requirements that apply to live conductors also apply to neutral for isolation purposes.
  • Chapter 46 (Isolation and switching), esp. 461.2 and 462.1 • 461.2: An installation must have a means of isolation that disconnects all live conductors (PEN excepted).
    • 462.1: Isolation must switch off all live conductors as required for the system.
    Relevance: The main switch for the installation must isolate all live conductors relevant to the installation. With two submains sharing a neutral, each submain neutral must be in series with a pole of the main linked switch (achieved by splitting the neutral on the supply side as in Diagram 1).
  • Section 537 (Isolation and switching) — 537.2 (Isolation) • 537.2.1.1/537.1.x series: Devices for isolation must disconnect all live conductors; the neutral is treated as a live conductor for isolation.
    Relevance: Using a 4‑pole linked switch and feeding each neutral through its own pole complies with the isolation function. Diagram 2 compromises that by effectively paralleling the neutral poles when ON.

METER2.pngMETER.png
 
Either of those perform the same function.

But a third suggestion would be to use 2 x 2 pole isolators.
Then you could, for example, isolate the off peak CU without affecting the general power and lights.
 
Either of those perform the same function.

But a third suggestion would be to use 2 x 2 pole isolators.
Then you could, for example, isolate the off peak CU without affecting the general power and lights.
So they both function the exact same way but there is no definitive this or that answer, just comes down to the installers preference?
 
Personally, i dont like having unused terminals like your second diagram.... and most 4 pole isolators ive seen are marked, either from factory, or added to, with L1,L2,L3,N .... which wouldn't be right with 2 L's and 2 N's

With everything being sized correctly... the only difference is the N being split before or after the isolator
 