Hello everyone, first post here. I can really find a definitive answer to this question so thought I'd ask here.
I've drawn 2 wiring diagrams showing a single phase supply, I'm wondering which one of these would be the best/most suitable instal method?
I have a few notes to point me in the right direction but I want a definitive answer.


I've drawn 2 wiring diagrams showing a single phase supply, I'm wondering which one of these would be the best/most suitable instal method?
I have a few notes to point me in the right direction but I want a definitive answer.
- Part 2 Definitions: “Neutral conductor” is a live conductor. Why it matters: Requirements that apply to live conductors also apply to neutral for isolation purposes.
- Chapter 46 (Isolation and switching), esp. 461.2 and 462.1 • 461.2: An installation must have a means of isolation that disconnects all live conductors (PEN excepted).
• 462.1: Isolation must switch off all live conductors as required for the system.
Relevance: The main switch for the installation must isolate all live conductors relevant to the installation. With two submains sharing a neutral, each submain neutral must be in series with a pole of the main linked switch (achieved by splitting the neutral on the supply side as in Diagram 1). - Section 537 (Isolation and switching) — 537.2 (Isolation) • 537.2.1.1/537.1.x series: Devices for isolation must disconnect all live conductors; the neutral is treated as a live conductor for isolation.
Relevance: Using a 4‑pole linked switch and feeding each neutral through its own pole complies with the isolation function. Diagram 2 compromises that by effectively paralleling the neutral poles when ON.