Thanks Richard. Yes - mid level floor - acoustic & fire protection. Don't seem to be able to get 25A RCBOs for this contactum CU. Looking at Tuttle's picture, this is good enough for B in my opinion (which I would be happy to put 4mm on a 32A breaker as CCC quoted at 30A is near enough given other positive variables) My problem is I'm installing from below, and so later when the insulation is installed who knows how far up it could be pushed. Summary - I would be happy with Tuttle's installation, but am going to put ply under cables to prevent the insulation being squashed higher into cabling....hope that makes sense....thanks for all the great replies/help
 