oldie

Does anybody know exaclty what the Building Regs are for the distance of Electric Cooker Isolation Switch from Gas Hob?
I have been given 150mm 250mm 300mm The last Building Inspector I spoke with said "I seem to recall seeing 30cm written somewhere"!
I know the rough guide is "A Pan Handle" but it would be nice to know if the goal posts are moving quicker than I am.

Point two concerns the ring main serving the kitchen is there a new regulation stating that the kitchen MUST be on a separate and independant ring serving only kitchen appliance? This applies even if the Consumer Unit is the latest 17th Ed.
 
300mm or more is the guidance

no new reg, can run of house ring if not overloaded
 
Last edited by a moderator:
300mm. Where is your building regs book you naughty naughty person :D

The separation of the kitchen from the rest of the house would be determined by the designer. Pointless if the property is like the one I live in where only a kitchen and lounge are downstairs :thumbsup
 
hmm, wondered why i couldn't find it in the Beano Annual.
 
i dont have new Beano Annual...! im still; working from 1995 and Dandy 2001
 
Last edited by a moderator:
had one last week where the client wanted a cooker supply, changing from gas to electric. there was only 5" between the cooker and the back door. only way i could do a reasonable job was to fit the cooker isolator high level, 1/2 above door frame and drop to CCU from there.
 
While the picture in the EGBR shows a distance of 300mm between cooker and switch, the text only refers to the switch not being located directly above the cooker. The kitchen refurb job I'm currently looking at has the existing switch 150mm away from the cooker. And that's where it's staying :smiley2: (it's been fine for 40 years I'll hasten to add. And there's not enough slack in the 7/064 to move it!)
 
The kitchen refurb job I'm currently looking at has the existing switch 150mm away from the cooker. And that's where it's staying :smiley2: (it's been fine for 40 years I'll hasten to add. And there's not enough slack in the 7/064 to move it!)

So you're not making it any worse than it already was then are you;)

Just like you can rewire an old property at existing heights for sockets and light switches.

:thumbsup
 