Morning everyone

ive been asked to calculate the maximum demand for a conversion of commercial property to 12 one bed self containted flats. There will be no gas service available. Each flat will consist of a 32 amp socket, 45 amp shower, 32 amp cooker, 20 amp electric radiators, 16 amp water heater and 6 amp lights. 1 landlord supply, loading not yet known.

After applying diversity of all loads x 0.4 60.4 amps per flat, this dosnt seem enough for all electric install, should I use onsite guides allowances.


60.4 x 13 = 785.2 x 230= 180.569 W to convert the watts to Kva is the calculation 180,000/ 1000 = 180Kva.

Are my calculations correct, or am I dumber than I think. Lol
 
that's about 62.5 amps per flat. your cooker and shower alone exceed that!

Totally agree, I would think 125 amp by using onsite guides allowances.

My knowledge isn't to great on Totalling Kva, I've turned the job down anyhow. I priced up for a electrical engineer to design, calculate and plan the infasturture. The client dosnt think this is needed. My knowledge is limited to single phase domestic installs. Getting ahead of my abilities I think.

Thanks for your reply.
 
Always a pain to turn down work, but at least you realised your limits before commiting to the job, I think the way you had priced would be best as it may have cost you more if you get your calculations wrong.
 
Hi,

Totally agree with Chrish, As E54 and Tony pointed out in another thread , correct diversity is not for the faint hearted; and if you get it wrong on a block of 12 flats your'e definitely in the poo. In this circumstance I think you gave the customer the best advice, that is , have the calcs done by a Professional Engineer.

Regards.
 