6.2 KWH x 12.44p = £18.51 per day, wow! £6,756.15 nice...
Ok so one more thing then if you would be so kind?
So if a server hosting rack (a metal cabinet full of PCs) has 2.4KVA electricity supplied with it, then why don't they just use Watts?
Do I then have to apply the power factor to it average 0.87 so really they supply 2.1KWH?
Thats it after that, honestly!! Thanks very much for your help, its much appreciated.
the answer is in the 'supplied with it'
whenever we talk about supplies we talk about VA because this is quite literally V supplied by amps available. Transformers and generators are normally rated in VA, (or realistically KVA.)
Of course, depending on what type of load you apply will depend how much of this VA (apparant power) you use as Watts (true power) and how much you just waste through inductive reactance
so if your load had a pf of 0.8, then for your 2.4KVa supply, then you could use 1.9Kw of true power
and to be honest, at this level its hardly worth worrying about.
if you were doing the same thing for a factory running at 500KVa, and by introducing over excited motors as synchronous capacitors to improve PF correction from say, 0.75 to 0.8, then you would be talking serious bucks !!!